This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Reduced low voltage 110V 16A socket circuits

Hi, I have been asked to provide 110V 16A sockets within a college workshop. The client is unable to advise of any equipment or loads that may be used and I am unsure of how many sockets to connect on a single circuit. I assume power tools will be connected for intermittent use. Does 2No. 110V 16A sockets on 1No. 20A Type C MCB radial circuit sound appropriate?....could you connect more on 1No. circuit, say 4No?....or would you provide 1No. 16A Type C MCB radial circuit per 110V 16A socket.

Thanks
Parents
  • Many thanks for the responses. The proposed locations are generally 2 sockets located together in a large workshop so 2 per circuit seems logical.
Reply
  • Many thanks for the responses. The proposed locations are generally 2 sockets located together in a large workshop so 2 per circuit seems logical.
Children