mapj1:
Is the building a locked enclosure accessible only by tool or key ?
If it really is early 60s (red, white & blue phases, not red, yellow & blue) then the whole double fault to danger mentality that we have today had not really developed, and yes exposed single insulated wiring would not have raised an eyebrow, especially behind a locked door. Actually earthing was also given less importance, (like none at all for lights), so that too may be a bit squiffy in terms of Zs and modern disconnection times.
(and no electronic loads, so reduced neutrals still in vogue for 3 phase supplies)
After all, bare busbars behind covers held by knurled brass thumb nuts, and light switches and ceiling roses where the covers span off by hand to reveal eminently touchable bare metal were very much still the order of the day. The current transformer secondary windings will not (I hope) be handling more than what today we would call ELV, though a primary to secondary winding short in a current transformer may not be detected if the metering wiring is not earthed on one side....
Had it been done later there might have been a removable perspex panel or something if the intention was to leave it visible to show no fiddling with the meter wiring.
I suspect even back then it was something of a special, but more or less in the spirit of the standards of the time.
M.
Hello Mike,
yes the intake room is padlocked. Should I get the metering company to improve the exposed single insulated 400 Volt wiring? The main supply tails are insulated and sheathed red, yellow and blue coloured. P.S.C.C. 1.5kA. E.F.L.I. 0.15 Ohms. Earthed by a 16mm2 black single that runs alongside the main underground armoured incommer.
Z.
mapj1:
Is the building a locked enclosure accessible only by tool or key ?
If it really is early 60s (red, white & blue phases, not red, yellow & blue) then the whole double fault to danger mentality that we have today had not really developed, and yes exposed single insulated wiring would not have raised an eyebrow, especially behind a locked door. Actually earthing was also given less importance, (like none at all for lights), so that too may be a bit squiffy in terms of Zs and modern disconnection times.
(and no electronic loads, so reduced neutrals still in vogue for 3 phase supplies)
After all, bare busbars behind covers held by knurled brass thumb nuts, and light switches and ceiling roses where the covers span off by hand to reveal eminently touchable bare metal were very much still the order of the day. The current transformer secondary windings will not (I hope) be handling more than what today we would call ELV, though a primary to secondary winding short in a current transformer may not be detected if the metering wiring is not earthed on one side....
Had it been done later there might have been a removable perspex panel or something if the intention was to leave it visible to show no fiddling with the meter wiring.
I suspect even back then it was something of a special, but more or less in the spirit of the standards of the time.
M.
Hello Mike,
yes the intake room is padlocked. Should I get the metering company to improve the exposed single insulated 400 Volt wiring? The main supply tails are insulated and sheathed red, yellow and blue coloured. P.S.C.C. 1.5kA. E.F.L.I. 0.15 Ohms. Earthed by a 16mm2 black single that runs alongside the main underground armoured incommer.
Z.