Old incomer connected to four 3 phase cutouts help

Hi all,


I have a very old incomer entering the building that then feeds to 4 x 3ph cutouts. You can see two of the 3ph cutouts in the pic.
9f8642aebed8db60e40f7a2578ffd3a3-original-02.jpg


The incomer says on it  - BI Callender's - 4E 150 x 3. I assume this means 3 x 150 Amps? Please do correct me if I am wrong.


1. What is the maximum power I can draw from this system?


2. If each of the 4 Three phase cutouts were loaded with 100 Amp fuses and I was to pull close to that from each fuse. what would happen to the incomer as this would equate to 1200 Amps!


3. Is connecting 4 3ph cutouts to this old beast a reasonable thing to do? Or is it ridiculous?


Many thanks

Simon
Parents


  • It may be worth verifying Zs is low enough to blow a 150Amp fuse before the DNO get there, so if it is not, you can get them to do something about that at the same time.



     


    I have a Zs of 0.22 measured from a distribution board 2 meters away from the incomer.


Reply


  • It may be worth verifying Zs is low enough to blow a 150Amp fuse before the DNO get there, so if it is not, you can get them to do something about that at the same time.



     


    I have a Zs of 0.22 measured from a distribution board 2 meters away from the incomer.