Had a callout to a block of flats last night where one of these devices (250A) had tripped. Cause seems to be a fault on a lift, as its own 100A downstream device also tripped, so obviously not set correctly for discrimination. Problem is that after restoring the 250A device it now trips on a very small load, literally a couple of amps per phase. Wondered if anyone has seen this before? has the trip unit been destroyed by the fault or has its electronics got into a pickle?


As it was night time there was not enough load to even light the micrologic display. As a temp clear I managed to move the circuit onto an unused 100A device in the panel but for 13 flats and the communals dont know how long ill get away with that.


PS can the trip units be replaced safely on these units without isolating the upstream device, this would be a 1600A ACB feeding a very large development.


Thanks in advance


Tom
Parents
  • Former Community Member
    0 Former Community Member
    Yes, the trip units are separate and removable and can be done in situ but Schneider were not very helpful about whether that can be done with the incoming terminals live but unit tripped, they just quote that is live working and we don't recommend it.It does look like the live parts are well away from from the trip unit when the switch is off. I will need to get that clarified though as the only thing between me and the DNO transformer is about 15ft of cable and a 1600A air circuit breaker.
Reply
  • Former Community Member
    0 Former Community Member
    Yes, the trip units are separate and removable and can be done in situ but Schneider were not very helpful about whether that can be done with the incoming terminals live but unit tripped, they just quote that is live working and we don't recommend it.It does look like the live parts are well away from from the trip unit when the switch is off. I will need to get that clarified though as the only thing between me and the DNO transformer is about 15ft of cable and a 1600A air circuit breaker.