DISTRIBUTOR CANNOT BE TRUSTED...

Former Community Member
Former Community Member
Hi folks!


This is my first forum post and hopefully and interesting topic. I am looking for some advice on where to start!

Background:
  1. 4th floor apartment tear-out in the city of Baku, Azerbaijan in a very old Soviet-era building block with unknown amounts of modifications.

  • 4 wire system (3-phase and neutral) entering and distributed throughout the building (no armoured cable / no separate earth).

  • No enforced local regulations as the general wiring in the city is a free-for-all (I am told it should be to PUE 6 standard). I could share many examples but this is not the aim of this post!

  • No building plans available from the council / no wiring / single-line diagrams available for the building or from the distributor.

  • No option available for a reliable survey - Partly being that most of the local electricians think that an earth core is a waste of money!

  • Basically the local distributor cannot be relied upon as can be seen by the photo example of the electrical panel closest to the apartment from the local government electrical company...

  • I am an electrical engineer wanting to get my hands dirty with my own project compliant to the BS 7671 wiring regs. I will design the domestic electrical installation and will have it verified by an (UK) electrician / expat before proceeding and sourcing materials.

Aim:


  1. Brand new domestic apartment electrical installation to BS 7671 18th Edition in which is in my control (full rewire, new consumer unit etc.). BS exceed the local regulations.

  • Keep politics / what-should-be for the incoming panel out of the discussion, it is what it is and there is not much I can do except wait decades for regulations and enforcements to catch up!

  • Provide the safest solution to protect my family without running away from the building / country.

Closest Panel to my Apartment:

  • Ok lets cut to the chase - this may just be the worst panel that you have ever seen however I cannot modify it as it is owned by the local government electrical company. It gets no points for compliance to any regulation (maybe 1 for being metal only!). I unfortunately has to live with this monstrosity until the building is knocked down in the future (and this is one of the newer / better panels in the building believe it or not…1 of 3 panels up to the apartment).

34853545ae5c04645e1bb134ec9267e3-img_1749.pdf


Queries:

  1. Can I assume that the incoming supply is a TN-C-S (and I know this is the distributors responsibility…) i.e. connect the MET and neutral together before the consumer panel? I know we should never assume so what is the best way to test? I am trying to source a Megger. My concern is that this could bypass some protection elsewhere in the building although it appears to have only overcurrent protection (fuses).

  • Should I have a dedicated earth run from the incoming of the building (from the neutral bar) up to the apartment consumer unit instead? My concern is that there my be a potential difference between the neutral and the earth at the apartment which could require 2P RCBOs throughout. Yes there should not be a potential difference however there is a lot of twisted wiring (junction boxes are a luxury…) and poor looking connections as well as all the apartment neutrals connected together in the block.

  • A third option would be to have an earth pit installed in the car park and run the dedicated earth to the MET in the apartment although 2P RCBOs may still be required.



Any assistance is greatly appreciated including verification / testing methods before I dive into the design of the consumer unit. Thank you in advance,


Chris
Parents
  • An example of the better earth problem - not quite in the UK, but almost, as Lyle works in Ireland, and it certainly is could happen here. There are a few very crummy TT installs with pole-pig transformers that only feed one or two farm buildings in the UK.


    The POE (not PoE !!!) tends to be to supply specific types of equipment, not something you buy off the shelf, and exactly what goes in green painted boxes varies a bit ( and is not really for discussion here !), but the principles apply universally. - imagine what may happen if an army rocks up in a strange place and needs power for the patrol base or small forward operating bases as soon as possible. If for example a small group is setting up inside existing buildings, then there may well be most of an electrical installation present, and it   may be quicker to get that working somehow than to wait for generator trucks, fuel etc that all give away your position. However, it makes the connector of opportunity to be something like the M6 wing nut and to design equipment to be used in a situation like that then almost no  assumptions are made about the reliability of the upstream supply, polarity, voltage or continuity.

    An all pole breaking RCD at the incomer is a good start, good, along with some sort of external earth connection- which at the FOB may be associated with comms antennas /equipment. Either a direct N-E bond or via a capacitor after the RCD will trip the RCD if the neutral voltage is too far off earth or if the LN are reversed - which you have to assume can happen at any time as other things may be severed and reconnected outside.  Then under-voltage and over-voltage trips will guard against the worst errors such as being fed 2 phases instead of one phase and a neutral, though if possible small electronics equipment is designed to work OK from less than 100V to over 400V so that we do not really care to much.

    Note that there are situations where driving an earth electrode is not desirable,  the most extreme example would be suspected buried ordnance, but in a more domestic setting,  to buried strike water and gas pipes could be almost  as disappointing. Then you may put some metal plate or mesh into a puddle and then park the truck on it.

    I'm not sure that you are in quite the same situation, but some aspects apply.

    Mike.



Reply
  • An example of the better earth problem - not quite in the UK, but almost, as Lyle works in Ireland, and it certainly is could happen here. There are a few very crummy TT installs with pole-pig transformers that only feed one or two farm buildings in the UK.


    The POE (not PoE !!!) tends to be to supply specific types of equipment, not something you buy off the shelf, and exactly what goes in green painted boxes varies a bit ( and is not really for discussion here !), but the principles apply universally. - imagine what may happen if an army rocks up in a strange place and needs power for the patrol base or small forward operating bases as soon as possible. If for example a small group is setting up inside existing buildings, then there may well be most of an electrical installation present, and it   may be quicker to get that working somehow than to wait for generator trucks, fuel etc that all give away your position. However, it makes the connector of opportunity to be something like the M6 wing nut and to design equipment to be used in a situation like that then almost no  assumptions are made about the reliability of the upstream supply, polarity, voltage or continuity.

    An all pole breaking RCD at the incomer is a good start, good, along with some sort of external earth connection- which at the FOB may be associated with comms antennas /equipment. Either a direct N-E bond or via a capacitor after the RCD will trip the RCD if the neutral voltage is too far off earth or if the LN are reversed - which you have to assume can happen at any time as other things may be severed and reconnected outside.  Then under-voltage and over-voltage trips will guard against the worst errors such as being fed 2 phases instead of one phase and a neutral, though if possible small electronics equipment is designed to work OK from less than 100V to over 400V so that we do not really care to much.

    Note that there are situations where driving an earth electrode is not desirable,  the most extreme example would be suspected buried ordnance, but in a more domestic setting,  to buried strike water and gas pipes could be almost  as disappointing. Then you may put some metal plate or mesh into a puddle and then park the truck on it.

    I'm not sure that you are in quite the same situation, but some aspects apply.

    Mike.