Hi folks!


This is my first forum post and hopefully and interesting topic. I am looking for some advice on where to start!

Background:
  1. 4th floor apartment tear-out in the city of Baku, Azerbaijan in a very old Soviet-era building block with unknown amounts of modifications.

  • 4 wire system (3-phase and neutral) entering and distributed throughout the building (no armoured cable / no separate earth).

  • No enforced local regulations as the general wiring in the city is a free-for-all (I am told it should be to PUE 6 standard). I could share many examples but this is not the aim of this post!

  • No building plans available from the council / no wiring / single-line diagrams available for the building or from the distributor.

  • No option available for a reliable survey - Partly being that most of the local electricians think that an earth core is a waste of money!

  • Basically the local distributor cannot be relied upon as can be seen by the photo example of the electrical panel closest to the apartment from the local government electrical company...

  • I am an electrical engineer wanting to get my hands dirty with my own project compliant to the BS 7671 wiring regs. I will design the domestic electrical installation and will have it verified by an (UK) electrician / expat before proceeding and sourcing materials.

Aim:


  1. Brand new domestic apartment electrical installation to BS 7671 18th Edition in which is in my control (full rewire, new consumer unit etc.). BS exceed the local regulations.

  • Keep politics / what-should-be for the incoming panel out of the discussion, it is what it is and there is not much I can do except wait decades for regulations and enforcements to catch up!

  • Provide the safest solution to protect my family without running away from the building / country.

Closest Panel to my Apartment:

  • Ok lets cut to the chase - this may just be the worst panel that you have ever seen however I cannot modify it as it is owned by the local government electrical company. It gets no points for compliance to any regulation (maybe 1 for being metal only!). I unfortunately has to live with this monstrosity until the building is knocked down in the future (and this is one of the newer / better panels in the building believe it or not…1 of 3 panels up to the apartment).

34853545ae5c04645e1bb134ec9267e3-img_1749.pdf


Queries:

  1. Can I assume that the incoming supply is a TN-C-S (and I know this is the distributors responsibility…) i.e. connect the MET and neutral together before the consumer panel? I know we should never assume so what is the best way to test? I am trying to source a Megger. My concern is that this could bypass some protection elsewhere in the building although it appears to have only overcurrent protection (fuses).

  • Should I have a dedicated earth run from the incoming of the building (from the neutral bar) up to the apartment consumer unit instead? My concern is that there my be a potential difference between the neutral and the earth at the apartment which could require 2P RCBOs throughout. Yes there should not be a potential difference however there is a lot of twisted wiring (junction boxes are a luxury…) and poor looking connections as well as all the apartment neutrals connected together in the block.

  • A third option would be to have an earth pit installed in the car park and run the dedicated earth to the MET in the apartment although 2P RCBOs may still be required.



Any assistance is greatly appreciated including verification / testing methods before I dive into the design of the consumer unit. Thank you in advance,


Chris
Parents
  • It will be near impossible to install a new TT earth electrode in the car park / yard away from underground metalwork. I need to continue my homework on rebar electrodes and distances away from other buried services. Would it be such an issue in a flat with no extraneous connections for the TT earth electrode to be in close proximity to buried metal work? If a fault from another system were to raise the ground potential then all the exposed metalwork in the flat should also raise to the same potential i.e. no potential difference between exposed metalwork within the flat.

    The idea of keeping a TT earth separate from other earthing systems generally only applies where there's something about the other earthing system you wish to avoid - e,g. avoiding the dangers of PME earths when supplying caravans or EV charge points.


    If the other hand you're only using a TT system because a supplier's earth terminal isn't available (otherwise PME would have been fine) then there's little need to worry about segregating your earthing arrangements. Indeed it's quite common to have rural TT installations that have TN-like Zs values because there's a path via bonding to metallic water or gas pipes to a TN neighbour.


    As you say, if you can create an equipotential zone, the actual potential it is at is far less of a worry. In practice you can never create a perfect equipotential zone (especially if bits of the installation go outside!) But it seems you're in a far from ideal starting position so I think the best you can go is find some kind of reliable Earthing facility (local electrode or re-bar) and then bond everything within reach - including things that might be connected the dodgy supply 'Earth' if needs be. As far as possible using Class II equipment outdoors at ground level - or protected by insulating enclosures - can mitigate the risks there. Or you might consider a separated circuit for things like the water pump (i.e. unearthed, fed via an isolating transformer) - although if the pipework is metallic, it's probably pointless.


    Just bare in mind that if yours is the only installation in the area that does have proper bonds and the supply N/PEN does go faulty, you might end up carrying the return currents for most of the neighbourhood through your bonds - so generous oversizing might be the order of the day. Plastic plumbing can certainly help.


       - Andy.
Reply
  • It will be near impossible to install a new TT earth electrode in the car park / yard away from underground metalwork. I need to continue my homework on rebar electrodes and distances away from other buried services. Would it be such an issue in a flat with no extraneous connections for the TT earth electrode to be in close proximity to buried metal work? If a fault from another system were to raise the ground potential then all the exposed metalwork in the flat should also raise to the same potential i.e. no potential difference between exposed metalwork within the flat.

    The idea of keeping a TT earth separate from other earthing systems generally only applies where there's something about the other earthing system you wish to avoid - e,g. avoiding the dangers of PME earths when supplying caravans or EV charge points.


    If the other hand you're only using a TT system because a supplier's earth terminal isn't available (otherwise PME would have been fine) then there's little need to worry about segregating your earthing arrangements. Indeed it's quite common to have rural TT installations that have TN-like Zs values because there's a path via bonding to metallic water or gas pipes to a TN neighbour.


    As you say, if you can create an equipotential zone, the actual potential it is at is far less of a worry. In practice you can never create a perfect equipotential zone (especially if bits of the installation go outside!) But it seems you're in a far from ideal starting position so I think the best you can go is find some kind of reliable Earthing facility (local electrode or re-bar) and then bond everything within reach - including things that might be connected the dodgy supply 'Earth' if needs be. As far as possible using Class II equipment outdoors at ground level - or protected by insulating enclosures - can mitigate the risks there. Or you might consider a separated circuit for things like the water pump (i.e. unearthed, fed via an isolating transformer) - although if the pipework is metallic, it's probably pointless.


    Just bare in mind that if yours is the only installation in the area that does have proper bonds and the supply N/PEN does go faulty, you might end up carrying the return currents for most of the neighbourhood through your bonds - so generous oversizing might be the order of the day. Plastic plumbing can certainly help.


       - Andy.