Forgive me if this posted elsewhere here, but just came across the following on a Time Dissemination forum I frequent from a German poster.
On Jan.8, 13:04:54 UTC, the european grid frequency dropped from 50.0269Hz to a minimum of 49.7343Hz 13.4sec later, see fig 1 below, plot starting at 13:00, x-axis in sec. .
As a result southeast Europe was split from the rest, the frontier crossing the Balkan countries, see
https://www.entsoe.eu/news/2021/01/15/system-separation-in-the-continental-europe-synchronous-area-on-8-january-2021-update/
At 13:42:35 the western frequency was back at the 50Hz level, some time later they managed to resync the east and reconnected. Reasons are still under examination. A high western demand faced a southeastern production, so after the split the western frequency went down, the eastern frequency went up.
At 79/50 sec. after the event the primary control kicked in at 49.9035Hz and brought it up again to 49.9308 but eventually failed, see fig   2. below.
In the 13. hour that day they failed to deliver 112 sinewaves. Now ENTSO-E has to decide: readjust the wall clocks in Berlin or Athens?   )
Reportedly at a frequency below 49.8Hz big loads, like pumps for reservoirs or industrial customers are switched off automatically.
In 2011 the German Government launched a scenario for a blackout, detailed as a script:
https://www.tab-beim-bundestag.de/en/publications/books/petermann-etal-2011-141.html
Clive
f78d55e118b9b0d15fb9e7890397a312-huge-fig1.pngc
  • Sparkingchip:
    So, is the time in the UK still in sync with Western Europe?
    No, it never has been. All the links between the UK and Europe are DC, and the thyristor converter stations at either end of the links will operate at different frequencies.
    if there is an excess of generation, the frequency will rise. If there is too little generation, the frequency will drop. When the split occurred, there was too much generation on one side, and too little on the other side until they stabilised.
    In the UK, National Grid run the system to keep synchronous time. If you average the frequency over several days,
    Alan.
  • Life throws odd moments up.
    A few years ago a kitchen fitter got me to replace a consumer unit for a customer who worked for Alstom, I ended up having a  half hour HVDC masterclass with a cup of coffee, then later on I did similar with a guy who was high up National Grid who explained the AC system.
    There is all sorts of things that have been explained to me by customers who are experts in their fields.
  • Although in the UK perhaps surprisingly, it spends a shorter time close to frequency, and quite a lot of time either above or below and then flips between the 2 states,  plots of frequency density (that is the fraction of the time that each frequency component is present )
    show a slightly 'rabbit ears' distribution, with a depression in the centre and extending slightly on either side of perfect 50Hz.
    I have read an explanation for this in terms of the way the frequency control is done-  to avoid excessive switching, and associated costs , once connected, extra generation is not removed until clearly above the target, nor is extra added until clearly below.
    Even so, it is pretty tightly bunched. Genset owners can only dream of this sort of precision.
    A typical plot based on 1 minute cycle counts over a 24 hour period. If measured over shorter intervals, the variation is wider - you may see 49.7 or less or 50.3 or above for a few seconds during any one minute.
    M.