Chris Pearson:John Peckham:
BS 7671 has no provisions for Deviations. There is a however the provision for a Departure. A Departure is a deliberate act, it has to be no less safe that the requirements of BS 7671 and has to be recorded on the installation certificate, see Regulation 120.3.
BS 7671 does not recognise BS 7288 devices for fault protection or additional protection see Regulations 531.3.4.1 and 531.3.4.2. BS 7288 devices in my view cannot be used for additional protection or isolation as in the standard they have to be protected by an upstream RCD. So they are less safe than the provisions of BS7671 and cannot be used as a Departure."A BS 7288 socket outlet is better than nothing": discuss.
Although I'd given up so to speak on this BS7671/ EWR contravention observation (or whatever it is) regarding minor works, on the 'better than nothing' question and still linking into 7671 minor works, then I'd answer with, suggesting perhaps... in some situations.
In a bedroom upstairs (context matters?) , where another socket is required not too far from another (or another light point), I can't see that it (or RCD, or AFDD or any future additional protection) is really required for such minor works to be certified... and as said and again, I'd prefer if BS7671 accounted for these types of situations in general (domestic, commercial etc) as 'departures' doesn't strictly allow it, so one simply cannot sign off to BS7671 if work does not comply fully. There should be no law broken in such cases and we believe none would be.. oooerrr... in a non-virtuous realistic assessment ... and what could go wrong in any case in such a situation to be more unsafe from other sockets or light points in the same location.
Done. :-)
Best regards
Chris Pearson:John Peckham:
BS 7671 has no provisions for Deviations. There is a however the provision for a Departure. A Departure is a deliberate act, it has to be no less safe that the requirements of BS 7671 and has to be recorded on the installation certificate, see Regulation 120.3.
BS 7671 does not recognise BS 7288 devices for fault protection or additional protection see Regulations 531.3.4.1 and 531.3.4.2. BS 7288 devices in my view cannot be used for additional protection or isolation as in the standard they have to be protected by an upstream RCD. So they are less safe than the provisions of BS7671 and cannot be used as a Departure."A BS 7288 socket outlet is better than nothing": discuss.
Although I'd given up so to speak on this BS7671/ EWR contravention observation (or whatever it is) regarding minor works, on the 'better than nothing' question and still linking into 7671 minor works, then I'd answer with, suggesting perhaps... in some situations.
In a bedroom upstairs (context matters?) , where another socket is required not too far from another (or another light point), I can't see that it (or RCD, or AFDD or any future additional protection) is really required for such minor works to be certified... and as said and again, I'd prefer if BS7671 accounted for these types of situations in general (domestic, commercial etc) as 'departures' doesn't strictly allow it, so one simply cannot sign off to BS7671 if work does not comply fully. There should be no law broken in such cases and we believe none would be.. oooerrr... in a non-virtuous realistic assessment ... and what could go wrong in any case in such a situation to be more unsafe from other sockets or light points in the same location.