EWR (1989) - just for thought really on the point of decent Engineering Regs in ref. to Acts/Laws/Statute etc

There is no requirement under EWR to work to BS7671  (if that is not true, the following probably is rendered  irrelevant).


Scenario: its 2019 and there is no RCD protection for a socket recently added to an existing circuit. An unfortunate event happens (someone is electrocuted and dies; worst case) whilst using that socket and as a result the person who carried out the work is prosecuted, as it is argued the presence of the RCD would have prevented it happening. It must matter what that someone was doing when using that socket, so perhaps they were using a vac and ran over and already damaged cord (struggling here for a plausible scenario of something that could go wrong with a newly added socket/no RCD combo). Of course if someone was using other pre-existing socket then there is no case.


Under the EWR, how is it possible to prove legally (and reliably) that by working to other 'standards' (if EWR makes no reference to BS7671 - as it arguabky should never) at the time [of design/construction], was  the cause of the event and the person carrying out the work is at fault  ?    Is there ever going to be a case possible due to not having RCD - of course having RCD has additional protection benefits, but so does never ever going outside, so as to not get run over by a bus.


Im just using lack of RCD as an example on working to a standard not being BS7671 ...it could just as easily be someone designed, built and constructed a whole installation to their own standards - how is it legally decided those standards were not 'good' enough under the EWR (if BS7671 is not statutory as argubly it should never be) ?


(this is most likely in the wrong forum, but posted here as current practitioners to BS7671 might like to comment...or not :-)  )

Parents
  • Chris


    I feel sure you would have learned Part 1 sets out the Fundemental Principles, Part 4 sets out the safety rules and Part 5 is the how to do it section . Part 5 is Selection and Erection so tells as what type of RCD is to be selected . The Regulations in respect of the selection of RCDs are a shall not optional.  BS 7671 applies to new installations, alterations and additions. 


    So if we need to fit an additional socket to an existing circuit we can protect the socket locally with a BS EN 61008 device or a  BS EN 61009 device. Alternatively we can pull the ends of the ring or radial from the protective device in the board, install an RCD in an enclosure close to the board and re-connect the circuit to the RCD. 

Reply
  • Chris


    I feel sure you would have learned Part 1 sets out the Fundemental Principles, Part 4 sets out the safety rules and Part 5 is the how to do it section . Part 5 is Selection and Erection so tells as what type of RCD is to be selected . The Regulations in respect of the selection of RCDs are a shall not optional.  BS 7671 applies to new installations, alterations and additions. 


    So if we need to fit an additional socket to an existing circuit we can protect the socket locally with a BS EN 61008 device or a  BS EN 61009 device. Alternatively we can pull the ends of the ring or radial from the protective device in the board, install an RCD in an enclosure close to the board and re-connect the circuit to the RCD. 