EWR (1989) - just for thought really on the point of decent Engineering Regs in ref. to Acts/Laws/Statute etc

There is no requirement under EWR to work to BS7671  (if that is not true, the following probably is rendered  irrelevant).


Scenario: its 2019 and there is no RCD protection for a socket recently added to an existing circuit. An unfortunate event happens (someone is electrocuted and dies; worst case) whilst using that socket and as a result the person who carried out the work is prosecuted, as it is argued the presence of the RCD would have prevented it happening. It must matter what that someone was doing when using that socket, so perhaps they were using a vac and ran over and already damaged cord (struggling here for a plausible scenario of something that could go wrong with a newly added socket/no RCD combo). Of course if someone was using other pre-existing socket then there is no case.


Under the EWR, how is it possible to prove legally (and reliably) that by working to other 'standards' (if EWR makes no reference to BS7671 - as it arguabky should never) at the time [of design/construction], was  the cause of the event and the person carrying out the work is at fault  ?    Is there ever going to be a case possible due to not having RCD - of course having RCD has additional protection benefits, but so does never ever going outside, so as to not get run over by a bus.


Im just using lack of RCD as an example on working to a standard not being BS7671 ...it could just as easily be someone designed, built and constructed a whole installation to their own standards - how is it legally decided those standards were not 'good' enough under the EWR (if BS7671 is not statutory as argubly it should never be) ?


(this is most likely in the wrong forum, but posted here as current practitioners to BS7671 might like to comment...or not :-)  )

  • davezawadi (David Stone):

    It is necessary to have some kind of balance here, because "minor works" in particular should not have unexpected consequences for the customer who has to pay (and in some cases may not be capable of doing so). If major work is being considered the situation may be in a different light, but there is a problem with small domestic jobs. Let us say I need to extend a circuit as an example. There is no existing RCD protection, but also no particular risk. As the CU is old I cannot get an RCD or RCBO from the manufacturer, so should I change it, or fit an RCD in the tails? The only route is to ask the customer if they want RCD protection, but getting them to write the answer in a letter might be very difficult.  I have two choices, I can walk away (which probably means a less good DIY job) or I can do as they wish exactly with no RCD, or a possible third choice of the tails RCD at little or no cost. This is an ongoing problem with changes to BS7671, that it could be considered that the current version is the only one that is "safe" by the new definition and anything not complying is therefore "unsafe". Clearly, this is not a satisfactory situation and not one which should be faced by the Electrician. The modified circuit is no less safe than the original and therefore has to be satisfactory for use. However, a Lawyer might well try to argue the opposite, that it is the Electricians duty to make the circuit compliant with the latest edition of BS7671. This must not be allowed to become the case, as the safety cannot be controlled by the Electrician, if nothing else for financial and contractual reasons. The term "Designer" is being applied in a way that is not sustainable, mainly by the CDM regulations, because it implies that ALL the choices for the design are available to him, whereas in the case of Minor Works he has virtually zero choices.


    If it's a place of work (which it must be given the original question - otherwise we are talking about consumer protection legislation instead of EAWR), then this is covered by the "so far as reasonably practicable" I pointed out above ... if it really is a huge cost, that is. In a place of work, this is all balanced against the fact that some fines for H&S breaches are based on company turnover, and executives can also be personally prosecuted.


  • Perhaps another question, rather than BS 7671 or not, is which version of BS 7671.


    Work to BS 7671:2008 would have satisfied, for instance the EAWR 1989, back in 2010, and the legislation/statutory-regulations hasn't changed since - so why does it not satisfy the EAWR 1989 in 2021? (again considering that legislation is deliberately non-ambulatory).


       - Andy.
  • Thanks for the interest and input everyone.  It is difficult to pose such a question without some folks thinking there is some 'cop out' reason, or inexperience at play, or that one does not recognise safety improvements etc (and I am not implying any one has thought thus). My question wording is never the best so I accept if it reads as such and prompts such thinking. I'd rather people start from the premise it is about exploring ideas, catering for reality and that people participating are competent (in their scope) and caring about the work done etc.


    Essentially, DaveZ (and Im not implying there is any agreement with me) has got closer to an underlying issue that at least I think is important and why I posed the question. 


    Again, I apologise for poor wording but here goes:


    If working on an installation built to previous edition Regs and carrying out 'minor works', then it should still be possible to sign off such work as compliant with BS7671 if in the judgement of the engineer it is not less safe than when it was built. There should be scope within design and construction on older systems, at least for 'minor works', acknowledging in the engineers consideration, that implementing some more recent Regs aspect is 'uneccessary'.   EICR approach has a similar view - suggesting aspects could do with improvement to bring up to date etc. One might not condemn (unless other aspects led one to) an installation simply because it lacked RCD, AFDD or any other advancement... but one would suggest improvement (perhaps).  Such work should not result in "its unsafe" claims etc, ... unless it is actually unsafe from the engineering point of view and not for example due to non-addition of AFDD or RCD or whatever else comes along.


    If going beyond 'minor works', like adding a new circuit(s) or new [main/sub] board, then it would seem appropriate to design the new circuit to the latest Regs and of course new work. By the way, I wasnt in my question implying domestic or commercial, but just in general.


    Along with everyone in the industry and if it needs acknowleding for completeness, if conditions allow (e.g. replacing MCB with an RCBO) then one suspects most electricians would work to the latest, but if it is not possible, why can it still not be signed off to Regs with a note e.g. " complies except for one aspect of no RCD (or AFDD) present but everything else complies leaving the install no less safe then before"  , in the same way one might rarely write a Departure.


    I feel BS7671 is loosing some engineering reality in not accepting not everything might be possible and not allowing judgment.  If things are properly recorded, then why not.   As an aside and not wanting to start a new/old  flame off, why has a 'risk assessment crept in the BS7671.


    Of course some people might not agree with the above... but is that them just being idealistic... or is the above really unreasonable from a safety and engineering reality point of view.....   !



    (proof reader awol...sorry for spelling etc)
  • OK Andy I will bite.


    The 17th Edition permitted the use of a PME earthing system to be connected to a vehicle charging  point charging a vehicle outside without any special measures in domestic premises to prevent shock in the event of the loss of continuity of the supply neutral. Knowing what we know now was that a sensible measure and was it an improvement to public protection to remove that provision in the 18 th Edition?


    Each Edition of the Wiring Regulations increases improvements to public electrical safety. Some of the changes deal with technological changes to installations and connected equipment and some is event driven by tragic events. Each change to the Wiring Regulations goes out for public consultation for the public input. 


    Installations to to previous editions may have been acceptable based on the thinking of the day and the equipment available for protection.
  • 644.1.2 For an addition and/or alteration to an existing installation, any defect or omission that will affect

    the safety of the addition or alteration that is revealed during inspection and testing shall be corrected before the

    Certificate is issued.



    I take this mean that new work, even if done "properly", isn't ok if part of the existing installation makes the new work unsatisfactory. So for example adding a socket to an existing non-RCD circuit isn't satisfactory: the old work is making the new work unacceptable.


    This contrasts with for example replacing a CU: there is no obligation to fix up all the circuits connected to that CU to make them 18th-compliant, because the old work (the circuits) aren't making the new work (the CU) unsafe.


    So you need to add an RCD to comply with BS7671:2020. Whether not complying with BS7671:2020 is illegal, is of course another matter.
  • OK, an EICR on a new purchase shows that a complete re-wire is required. Stage 1, complete kitchen refurbishment because the house is uninhabitable otherwise. So new lights, sockets, and cooker circuit. CU does not comply with 17th+3 onwards. Do we sign off the new circuits, or have we got to wait until the whole house has been re-wired and a new CU fitted?


    Move forward to this covid era. Rewire required and some circuits are replaced. Then it all grinds to a halt 'cos the householder is shielding. Do we certify the work to date, or do we wait until some indeterminate date when the job can be finished.


    I don't think that everything has to comply with the latest BS 7671 all the time.


  • psychicwarrior:

    Thanks for the interest and input everyone.  It is difficult to pose such a question without some folks thinking there is some 'cop out' reason, or inexperience at play, or that one does not recognise safety improvements etc (and I am not implying any one has thought thus). My question wording is never the best so I accept if it reads as such and prompts such thinking. I'd rather people start from the premise it is about exploring ideas, catering for reality and that people participating are competent (in their scope) and caring about the work done etc.


    Essentially, DaveZ (and Im not implying there is any agreement with me) has got closer to an underlying issue that at least I think is important and why I posed the question. 


    Again, I apologise for poor wording but here goes:


    If working on an installation built to previous edition Regs and carrying out 'minor works', then it should still be possible to sign off such work as compliant with BS7671 if in the judgement of the engineer it is not less safe than when it was built. There should be scope within design and construction on older systems, at least for 'minor works', acknowledging in the engineers consideration, that implementing some more recent Regs aspect is 'uneccessary'.   EICR approach has a similar view - suggesting aspects could do with improvement to bring up to date etc. One might not condemn (unless other aspects led one to) an installation simply because it lacked RCD, AFDD or any other advancement... but one would suggest improvement (perhaps).  Such work should not result in "its unsafe" claims etc, ... unless it is actually unsafe from the engineering point of view and not for example due to non-addition of AFDD or RCD or whatever else comes along.


    If going beyond 'minor works', like adding a new circuit(s) or new [main/sub] board, then it would seem appropriate to design the new circuit to the latest Regs and of course new work. By the way, I wasnt in my question implying domestic or commercial, but just in general.


    Along with everyone in the industry and if it needs acknowleding for completeness, if conditions allow (e.g. replacing MCB with an RCBO) then one suspects most electricians would work to the latest, but if it is not possible, why can it still not be signed off to Regs with a note e.g. " complies except for one aspect of no RCD (or AFDD) present but everything else complies leaving the install no less safe then before"  , in the same way one might rarely write a Departure.


    I feel BS7671 is loosing some engineering reality in not accepting not everything might be possible and not allowing judgment.  If things are properly recorded, then why not.   As an aside and not wanting to start a new/old  flame off, why has a 'risk assessment crept in the BS7671.


    Of course some people might not agree with the above... but is that them just being idealistic... or is the above really unreasonable from a safety and engineering reality point of view.....   !



    (proof reader awol...sorry for spelling etc)


    Particularly in the case of a workplace, this is a very dangerous assumption. The legal duty is to address the risks. A risk assessment should be reviewed when there are changes in standards, legislation, and working practices ... so reliance on earlier versions of BS 7671 in a place of work is not necessarily a get-out clause.


  • Hello gkenyon


    What 'assumption' are you referring to please?


    And what of it is very dangerous ?


    In the context of not having RCD (ignore upcoming possible AFDD) on a circuit where 'minor works' take place e.g being an additional socket, on an installation circuit that complies in all other respects to current regs and entirely to previous (discon times OK, bonding OK etc) ....my contention is that it it ought to be possible to have some mechanism to sign such works off under bs7671. Its unrealistic to suggest a new consumer unit/db (or perhaps rcbo not poss) for some minor works and its not unsafe in all honesty is it (accepting it could be *more* safe with the additional protection).


    It feels that I stand in a minority on this one and there is unlikely to be provision, so I will have to stand down (reluctantly :-) )


    Perhaps there is no room for allowing for 'safe' pragmatism in bs7671 certification of work.







  • Another thought, I f you look at the BSI website, you will find that previous versions of BS7671, for example BS7671:2008 + A3, are marked as “withdrawn”: 


    Status : Superseded, Withdrawn   Published : January 2015  Replaced By : BS 7671:2018+A1:2020” 


    I am not sure how far you would get legally, installing or inspecting based on a withdrawn standard. 


    Regards,


    Alan.
  • "Scenario: its 2019 and there is no RCD protection for a socket recently added to an existing circuit. An unfortunate event happens (someone is electrocuted and dies; worst case)"


    The installer is to blame if the socket was installed recently, as its use can not be policed and unskilled users could run leads to dangerous locations such as outside or into a bathroom. An R.C.D. type socket (although frowned upon by some) could easily be installed.


    Z.