EICR failed missing trunking?

Former Community Member
Former Community Member

Hi,



I’ve just had an EICR done last week, One item I do not understand and would need an electrician or someone to help please. the EICR report says “MISSING TRUNKING WITH WIRES NOT SUPPORTED C2 SHED.” The cable is clipped on the wood wall in the shed. There are no exposed wires. And the shed is not on escape routes. Does cable need to be in trunking in order to comply with the electrical wire regulation? Is the code 2 correct for this situation?  please see photo.1ff9527a633c65202618bef88f7b0919-original-shed.jpg



Thank you for help


Parents
  • LV cables, with solid conductors, not supported adequately throughout their run BS7671:2018:Amd.1. Regulations 552.8.4, 552.8.5 and 521.10.202 Code C2.


    Wiring system susceptible to external influences which may lead to potential danger, throughout its normal operation, due to poor workmanship and sub-standard installation practices. BS7671:2018:Amd.1. Regulation 134.1 Code C2.


    Wiring system not adequately protected against mechanical stress e.g. by impact, abrasion, penetration, tension or compression during use. BS7671:2018:Amd.1. Regulations 552.6.1 and 552.6.2 Code C2.
Reply
  • LV cables, with solid conductors, not supported adequately throughout their run BS7671:2018:Amd.1. Regulations 552.8.4, 552.8.5 and 521.10.202 Code C2.


    Wiring system susceptible to external influences which may lead to potential danger, throughout its normal operation, due to poor workmanship and sub-standard installation practices. BS7671:2018:Amd.1. Regulation 134.1 Code C2.


    Wiring system not adequately protected against mechanical stress e.g. by impact, abrasion, penetration, tension or compression during use. BS7671:2018:Amd.1. Regulations 552.6.1 and 552.6.2 Code C2.