Then 701.415.2 States that supplementary bonding is required unless main bonding is in place and all circuits are protected by a 30mA RCD.
To me 701.411.3.3 seems to state an RCD is always required but 701.415.2 implies that if supplementary bonding is in place then an RCD is not essential.
I would be interested in your views.
Thanks
Alan
If all of the requirements of 701.415.2 (iv) (v) and (vi) are met than no supplementary bonding is required. An R.C.D. is required though.
The installation of an R.C.D. is a wise precaution with a shower circuit. I would recommend one.
Z.