S.W.A. Puzzler.

You are to use two three core S.W.A. cables connected in parallel. Same size conductors and same length. The supply from source to load is single phase. If just using the steel wire armour as the C.P.C.s how would you arrange the six live cores to use them all for the single phase supply avoiding problems?


Z.
Parents
  • 3 line in one cable and 3 neutral in the other ?  So effectively two screened or earthed singles  ? 



    Gary
Reply
  • 3 line in one cable and 3 neutral in the other ?  So effectively two screened or earthed singles  ? 