This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

S.W.A. Puzzler.

You are to use two three core S.W.A. cables connected in parallel. Same size conductors and same length. The supply from source to load is single phase. If just using the steel wire armour as the C.P.C.s how would you arrange the six live cores to use them all for the single phase supply avoiding problems?


Z.
Parents Reply Children
No Data