nicemark:
I have been arguing about the methods of separating out the ends of twin and earth cable.
An old accepted trade method was to simply grip the earth wire and tear it out of the insulation to split the ends open.
However this puts considerable strain on the earth wire and in the case of 1mm wire it is very easy to stretch a significant amount.
I was wondering if you there is data or evidence to demonstrate that this method is not acceptable.
I have been an electrician for many years. I normally squeeze the P.V.C. T&E sheath with pliers so that it breaks at the end, then I recover the C.P.C. and use it as a cheese cutter wire to strip the cable back to the required length. I have never had a C.P.C. break or stretch. Some people use a knife and cut, or partially cut, down the middle of the sheath first. Only 1.0mm2 & 1.5mm2 T&E cables uses a 1.0mm2 sized C.P.C. others use a 1.5mm2 C.P.C. so it is stronger. The 1.0mm2 T&E or 3 core and C.P.C. has very thin weak sheathing so is easy to strip back. On site it is all about speed and efficiency. We do not need to clutter up our tool boxes with expensive unnecessary tools.
Rob Eagle:
I don't think you will have a problem, a quick back of a fag packet calculation tells me to stretch a 10cm length of 1mm2 by 1mm you would need 12.6 MN force which you would need a hefty machine to do that. Furthermore, the force you apply to strip is not true tensile as your curling it as you strip therefore adding a sheer force too, so between tensile and sheer you will be perfectly OK.
If you can stretch a length of 1mm2 copper wire with your hands you're a very strong lad!
Something slightly wrong with your units there.
I must get my entry in for The World's Strongest Man 'cos I just stretched a piece of 1 mm² wire and then it broke where it was wrapped around my pliers.
Mind you, the force was considerably more than needed to cheesewire through PVC sheathing.
Rob Eagle:
"Something slightly wrong with your units there."
12.6 Mega Newton force, 12.6 x 10^6.
How much longer did the wire become after stretching it by hand, or did you just get out the kinks? It broke at the pliers due to the edge of the pliers cutting into the soft copper, a significantly much lower force is required to do that.
That's the force exerted by gravity on about 1000 tonnes, so your wee copper wire will lift a small ship will it?
I tried again. The 1 mm² wire stretched by 30% before it broke in the stretched part, not at the pliers.