This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Underfloor heating regulations - EICR

Former Community Member
Former Community Member
Hi guys 


If underfloor heating has been fitted and basically just spured off from the ring straight to the thermostat, would that need to be flagged on a EICR? 


We don't know who manufactured it, so can't check their recommendations on this particular make and model


Seems a bit rough to me - Feel to flag as I would have wired via an FCU 


Thanks
Parents
  • Former Community Member
    0 Former Community Member
    AJJewsbury:

    What sized wiring is involved? I don't see anything smaller than 1.5mm² necessarily being satisfactory on a B32 for faults (including c.p.c.s - so 1.5mm² T&E with a 1.0mm² could be a problem).

       - Andy.


    2.5mm from the socket to the thermostat mate - 


Reply
  • Former Community Member
    0 Former Community Member
    AJJewsbury:

    What sized wiring is involved? I don't see anything smaller than 1.5mm² necessarily being satisfactory on a B32 for faults (including c.p.c.s - so 1.5mm² T&E with a 1.0mm² could be a problem).

       - Andy.


    2.5mm from the socket to the thermostat mate - 


Children
No Data