Downstream rcd tripping

Afternoon all, I had abit of a funny one this morning. Carrying out some work at a block of flats. 

DId a Ze at the landlords board to find the main earth had been cut off! Did a Ze between the live and the stub left on the side of the ryefield. This then tripped out some of the downstream RCDs feeding tenants flats. I assume that I'd in balanced the neutral. Just wondering if anyone else had had this.

I've called in ukpn to check the earthing and to get it fixed.
Parents
  • Hi MapJ

    thanks for the response. I can well imagine there will be some remedial works required. Though from what I've seen so far, it's all ok, except the lack of earthing. There aren't any water heaters, only sockets, lights and cooker per flat. 

    The landlord is abit of a DIY type so could well be something hidden.
Reply
  • Hi MapJ

    thanks for the response. I can well imagine there will be some remedial works required. Though from what I've seen so far, it's all ok, except the lack of earthing. There aren't any water heaters, only sockets, lights and cooker per flat. 

    The landlord is abit of a DIY type so could well be something hidden.