The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Location of Pull cord for shower isolator outside zones but could still be touched.

Former Community Member
Former Community Member
Hi 


Sorry if this is a bit of a basic question, I am still in training as an electrician and trying to make sure I understand how rules are applied in practice.


I have been thinking about where shower isolator pull cord switches can be installed following section 701 in BS7671 and having looked at a few other books I am a bit confused as my interpretation of the rules doesn't match what I would consider as common sense.


From my understanding a pull cord switch can be mounted above zone 1 with the insulated cord dropping in to zone 1 and as the switch is outside the zones it doesn't need anything beyond standard IP2x protection based on 701.512.3.

Zone 1 extends to 225 above the fixed floor height or where the shower head is fixed at a height greater than 225 then zone 1 extends to the height of the shower head. There doesn't appear to be any mention of extending the zones if the shower head is not fixed and in theory could be directed at the ceiling.


The bit that doesn't make sense to me is that there are lots of precautions to keep water and electricity separated and to prevent people coming in to contact with electricity when wet. If my interpretation is correct a pull cord switch can be mounted above the shower basin at 225cm, which I as an average height person can touch quite easily, especially as the height appears to defined from the floor and not the shower basin (fig 701.2(C)). Also if the shower head is not fixed it can be pointed directly at the switch. There doesn't appear to be any requirement to protect the switch against water ingress.


I know it's unlikely but I could spray the switch with water and then put my hand on it whilst holding a shower head that could presumably be connected to earth by the flexible pipe.


I know everything in a modern installation should be protected by bonding and RCD's but to me this feels fairly risky.


Is there something I am missing?


Thanks


Alan 

Parents
  • Alan B:

    I think in these situations my preferred approach would be rocker outside the bathroom or pull switch providing it's a reasonable distance from the shower.


    I am not quite sure why you need local isolation - doesn't the electric go off when the water goes off? ?


    However, if you must have it, and the doorway is two feet from the bath or shower basin (difficult to see how you could open a normal swinging door otherwise) you can put the switch there.


    More useful, of course, is the fan isolator, which can also be placed by the door, or even above it.


Reply
  • Alan B:

    I think in these situations my preferred approach would be rocker outside the bathroom or pull switch providing it's a reasonable distance from the shower.


    I am not quite sure why you need local isolation - doesn't the electric go off when the water goes off? ?


    However, if you must have it, and the doorway is two feet from the bath or shower basin (difficult to see how you could open a normal swinging door otherwise) you can put the switch there.


    More useful, of course, is the fan isolator, which can also be placed by the door, or even above it.


Children
No Data