mapj1:
I agree it probably goes against the intention of that regulation.
It's still out there, being driven across the dustier bits of the globe...
BS7671 is not written assuming that the supply could be derived from anything including things as rough as a pair of clips onto a bare overhead line, with some uncertainty about which core is which.
Power of opportunity brings a different set of risks and mitigations for which some of the standards assumptions are not so suitable, it does not mean you cant use the local electricity safely, you just have to plan for some odder cases - oh and never use any of the supply cables as earth.
You probably won't like my torch bulb NE as tell-tale indicator of lost neutral - if it lights up you have a bit of an NE offset problem if the filament has vaporised you have a big problem (or at least did have at some point since it was installed ).
What is the torch bulb Voltage please Mike. I am asking for a friend.
Zoomup:AJJewsbury:
I wouldn't expect SPD to offer any protection from longer-term overvoltage situations like broken neutrals - they operate by creating a low impedance L-PE or L-N and would have to dissipate huge amounts of (heat) energy if the overvoltage lasted for more than a small fraction of a second. The best we can hope for is that the SPD fails safe and disconnects itself before it starts a fire.
As for other solutions there are plenty of voltage monitoring relays on the market that could be fitted (probably via a contactor) to disconnect the installation if the voltage went outside limits. (e.g.https://uk.rs-online.com/web/p/monitoring-relays/9143945/ )
- Andy.Good morning Andy, how do we connect one of these to a single phase installation? Just use one phase terminal of the three available? Or are there single phase versions available?
Yes plenty of single phase versions available - e.g. https://uk.rs-online.com/web/p/monitoring-relays/1026131/ (this particular one complete with adjustable delay function too)
AJJewsbury:
I don't know whether I am being naïve here, but could one of these devices be used (along with a suitable contactor) for an EVCP? If not SP, perhaps TP?