AJJewsbury:
I wouldn't expect SPD to offer any protection from longer-term overvoltage situations like broken neutrals - they operate by creating a low impedance L-PE or L-N and would have to dissipate huge amounts of (heat) energy if the overvoltage lasted for more than a small fraction of a second. The best we can hope for is that the SPD fails safe and disconnects itself before it starts a fire.
As for other solutions there are plenty of voltage monitoring relays on the market that could be fitted (probably via a contactor) to disconnect the installation if the voltage went outside limits. (e.g.https://uk.rs-online.com/web/p/monitoring-relays/9143945/ )
- Andy.
Good morning Andy, how do we connect one of these to a single phase installation? Just use one phase terminal of the three available? Or are there single phase versions available?
Z.
Zoomup:AJJewsbury:
I wouldn't expect SPD to offer any protection from longer-term overvoltage situations like broken neutrals - they operate by creating a low impedance L-PE or L-N and would have to dissipate huge amounts of (heat) energy if the overvoltage lasted for more than a small fraction of a second. The best we can hope for is that the SPD fails safe and disconnects itself before it starts a fire.
As for other solutions there are plenty of voltage monitoring relays on the market that could be fitted (probably via a contactor) to disconnect the installation if the voltage went outside limits. (e.g.https://uk.rs-online.com/web/p/monitoring-relays/9143945/ )
- Andy.Good morning Andy, how do we connect one of these to a single phase installation? Just use one phase terminal of the three available? Or are there single phase versions available?
Z.
Single phase installation definitely have limitations in this respect:
mapj1:
I have fitted capacitors N-E after a 4 pole RCD, so that if the NE voltage rises, the RCD sees the N-E current and fires and breaks everything but the CPC.
Just interested on people's views as to whether this stacks up with Regulation 531.3.1.202 ?
531.3.1.202 It is not permissible to introduce an external connection for the purpose of intentionally creating a residual current to trip an RCD.
However, I am compelled to point out that I'm asking this question with the full knowledge that many appliances have a capacitor connected between N and PE - but we are talking about of orders of magnitude difference in capacitance (1-10 nF in appliances, vs perhaps 10-20 μF to trip a 30 mA RCD for an N-E voltage of 50 V)?
Just edited to note that this Regulation was introduced in BS 7671:2018, and therefore I'm not necessarily saying that Mike's application was non-compliant at the time.