This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Capacitive reactance in twin and earth

Former Community Member
Former Community Member
I'm after some information regarding the cause of capacitive reactance which is part of the overall impedance of a circuit when carrying out loop impedance testing. 


I am not an electrician so apologies if this is standard knowledge to some of you. 


I understand how a capacitor works and what capacitance is. Since capacitive reactance is part of the three types of "resistance" of a circuit I am assuming that the reason this capacitive reactance is included is because twin and earth can to a lesser extent behave like a capacitor even when laid flat and not coiled? With AC power in the conductors I'm assuming that an weak electric field of attraction between the two conductors separated by the wire insulation forms. When the AC emf  passes the peak of the emf in the sine wave and current "flow" is now in the opposite direction from what it was moments beforehand then the induced emf created by the electric field between the two conductors results in a small reactive current flowing in opposing direction to the main current hence capacitive reactance?


 Thanks in advance
Parents
  • Former Community Member
    0 Former Community Member
    Inductance per unit length is a measure of the energy stored in magnetic fields around moving charges (currents) and for that typical cable again is about 1 micro henry per metre if only one core is carrying current; but if the currents in the cable are balanced so current in  L = minus current in N the round loop inductance is quite a lot less than the sum of the inductances of the two cores, as the magnetic fields oppose and overlap and partly  cancel - the figures Dave quoted are for a line pair.



    Thanks , didn't know that either but makes perfect sense.
Reply
  • Former Community Member
    0 Former Community Member
    Inductance per unit length is a measure of the energy stored in magnetic fields around moving charges (currents) and for that typical cable again is about 1 micro henry per metre if only one core is carrying current; but if the currents in the cable are balanced so current in  L = minus current in N the round loop inductance is quite a lot less than the sum of the inductances of the two cores, as the magnetic fields oppose and overlap and partly  cancel - the figures Dave quoted are for a line pair.



    Thanks , didn't know that either but makes perfect sense.
Children
No Data