Federal Electric Stab-Lok MCBs Information

Former Community Member
Former Community Member


Hi Folks,


I am currently doing an EICR on a large site, with many old Federal Electric boards with the Stab-Lok type MCBs. I think they would have been installed circa 1980.


I have been scouring the internet and these forums in particular for manufacturers details, specifically for type 4 Federal MCBs. There have been consistent figures posted throughout but I would like to get my eyes on a datasheet, or any other information that's floating about, if it was possible that any you may still have that kind of information in your archives!

 

Apologies if this is a somewhat repetitive subject as I have seen many threads over the years asking the same details. 


Cheers,


Andrew
Parents
  • Here we go.


    For 0.4s disconnection times in ohms to comply with the 18th Edition.


    5A - 4.13     10A- 2.06    15A- 1.38    20A - 1.03    25A - 0.83    30 A - 0.68    40A - 0.51


    For 5s disconnection times in ohms to comply with the 18th edition.


    30A - 2.08   40A - 1.56    50A - 1.24    60A  - 1.04   80A -  0.78   100A  - 0.62

Reply
  • Here we go.


    For 0.4s disconnection times in ohms to comply with the 18th Edition.


    5A - 4.13     10A- 2.06    15A- 1.38    20A - 1.03    25A - 0.83    30 A - 0.68    40A - 0.51


    For 5s disconnection times in ohms to comply with the 18th edition.


    30A - 2.08   40A - 1.56    50A - 1.24    60A  - 1.04   80A -  0.78   100A  - 0.62