The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Sub main and TT

I am dismayed that I have to ask but it is so long since I worked in a TT area that I am doubting myself.

I'm running an SWA submain to an outbuilding so instead of the usual switch fuse should I be using a 100mA S RCCB and a 63A mcb?

The armoured passing directly through the outside doesn't necessitate a 30mA RCD does it (as I have been so advised)

Apologies and thanks.

Parents Reply Children
No Data