OSG Standard Circuits - 3A lighting
As we are all using led lamps / fittings now it seems this should be a standard circuit.
3A MCB with 1.0/1.0 cable
Lighting circuits used to be based on 100w incandescent lamp / room at 1800 lumens which is equiv to 20w led.
What are the figures for max distance for a 3A type B using 1.0/1.0 as an addition in table 7.1 page 66 in OSG?
    Led switching discussed in this previous recent topic:
    https://communities.theiet.org/discussions/viewtopic/1037/27010?post_id=149029#p149029
  • geoffsd:
    Zoomup:
    geoffsd:
    Why? 1.00 sq.mm. T&E, method C, has a CCC of 16A.
    Why 1.0mm2?
    Hi Zoom.
    You have moved the question mark and completely altered the meaning of what I wrote.
    Hello Geoff. Were you not implying that a 16 Amp rated cable in the form of 1.0mm2 protected by a  B3 M.C.B. is too large, and smaller cables could be used?
  • Or that there is no good reason to use a B3 MCB; especially since AFAIK, 1 mm² is the smallest size of T&E.
  • No, in reply to the idea of using a 3A MCB on light circuits.
    Why (use a 3A MCB)?