As we are all using led lamps / fittings now it seems this should be a standard circuit.
3A MCB with 1.0/1.0 cable
Lighting circuits used to be based on 100w incandescent lamp / room at 1800 lumens which is equiv to 20w led.
What are the figures for max distance for a 3A type B using 1.0/1.0 as an addition in table 7.1 page 66 in OSG?
I wonder if many new L.E.D. lamps on one circuit may create a high initial inrush current when first turned on, that may trip a B3 breaker.
Z.
geoffsd:As we are all using led lamps / fittings now it seems this should be a standard circuit.
3A MCB with 1.0/1.0 cable
Why? 1.00 sq.mm. T&E, method C, has a CCC of 16A.
Why 1.0mm2?
Because it is readily available and commonly found. It is probably the smallest practical size to be used on site that will not easily break or be damaged too much by being chucked in, errr, I mean installed. We could use 1 Amp bell wire or alarm cable, but it may be broken by other trades bashing it, tugging on it or walking over it in their hob nail boots. Also 1.0mm2 allows for future extension to circuits without too much trouble.
But having said that, a 1.0mm2 copper conductor is easily broken if previously accidentally nicked or scored. Perhaps we should consider that.
Z.