John Peckham:
No you don't apply diversity to single loads, you apply it to distribution circuits and whole installations.
The circuit protection and cable CSA should meet the demands of the plated current and/or the manufactures specifications in their data sheet.
Of course you can put it on a bit of 1.5mm T&E with a 10A MCB if you like and it will probably be OK for most of the time but then you are not complying with the manufactures instructions see Regulation 134.1.1.
JP
You feeling OK this morning John?
Diversity on individual cooker final circuits is a long standing practice (built into the very regulations until not very long ago, but now relegated to guidance) - I'm sure most of us know the 100% of the first 10A, 30% of the remainder, plus 5A for a socket in the cooker control unit off by heart.
By (admittedly old) copy of the OSG even has separate tables 1A for final circuits and 1B for switchgear/distribution circuits.
, so perhaps OSG is a little out of date?