AJJewsbury:
Also the 50mm limit is just for cables running through holes in joists - it doesn't apply elsewhere e.g. in the general void.
- Andy.
That's interesting, because you are the second person to say this but this wasn't how I interpreted the detail in the on site guide, which says:
"Where a low voltage cable is installed under a floor or above a ceiling it must be run in such a position that it is not liable to be damaged by contact with the floor or ceiling or the fixings thereof. A cable passing through a joist, under floorboards or ceiling support must
(a) be at least 50 mm from the top or bottom, as appropriate, or"
Which I took to mean if a cable is passing through a joist or under floorboards or above a ceiling support.
Does it actually mean - "A cable when passing through a joist that has or will have floorboards or a ceiling attached to it must (a) etc " ?
This would explain why I am getting this answer of it doesnt matter where your cables are clipped to the joist.
aligarjon:
I have never interpreted it like that. I have always included the cables clipped along the joist as they could easily be nailed if someone misses with a nail or screw, which is pretty easy to do.
Gary
Interesting again! - So you include the clipped cable in the 50mm rule as per my original interpretation?