I just thought of something

I know it`s many years ago that I queried the age old saying that was taught in college etc as to the r1 & r2 cross connection to form a double loop and the statement was made that this gave the exactly the R1 + R2 reading of the whole ring when taken from any point on the ring.

My statement was that this statement was not quite right and the word "exactly" needs substituting with "substantially" (I think the error was about 6% which as 6% of an already small number was not a great worry and it was still a very good approximation fit for use).


Anyway to add to that,,it just occurred to me . If we leave connected and test at a spur then it adds the spur value to the (nearly) ring value so that`s usually OK too.

However that`s only for spurs near to ring midpoint.!

If we had a spur nearer to one ring end than to midpoint it would therefore give a missleadingly large R1 + R2 value.

Not normally an issue but in extreme cases too pessimistic and causing a headscratch.


Off course field errors and instrument errors give missleading readings too.


I`d say once we done the fig 8 for the ring we should really connect ring ends together then test R1 + R2 from ring origin to each spur end to get as truer reading.


I know, I should get out more


?
Parents
  • whjohnson:

    A cross-connected ring is easy to achieve for a diyer whom, upon lifting a floorboard below a socket, sees 2 x cables going to it and bridges them out in the mistaken belief that by doing so he is maintaining an actual ring. I am doing no more fault finding on stuff like this, but merely dropping the mcb rating from 32 to 20 and have done with it.


    So, if I understand you correctly the two ring cables going to a socket are "bridged out". I can not visualize this situation please explain further.


    Z.


Reply
  • whjohnson:

    A cross-connected ring is easy to achieve for a diyer whom, upon lifting a floorboard below a socket, sees 2 x cables going to it and bridges them out in the mistaken belief that by doing so he is maintaining an actual ring. I am doing no more fault finding on stuff like this, but merely dropping the mcb rating from 32 to 20 and have done with it.


    So, if I understand you correctly the two ring cables going to a socket are "bridged out". I can not visualize this situation please explain further.


    Z.