gkenyon:Chris Pearson:
I still wonder why anybody would use 4 mm² T&E for a ring.Minimum tabulated current carrying capacity Iz to be at least 20 A (Reg 433.1.204) and therefore from Table 4D5, Ref Method 101# or, where correction factors (such as grouping or ambient temp) might mess things up a little, Ref Methods A, 100#, 102#.
As per earlier comment re 6 sq mm .... you might struggle with some products to drop spurs off a 4 sq mm ring at a socket-outlet or other accessory to BS 1363 because of terminal constraints if the product meets the minimum requirements of the standard.
Graham, thank you. I see what you mean. I had thought do radial instead, but short of going up to 6 mm² (which as you say, is possible only with the better makes of socket) under those circumstances, it would be necessary either to downsize to a 20 A OCPD, or complete a ring.
gkenyon:Chris Pearson:
I still wonder why anybody would use 4 mm² T&E for a ring.Minimum tabulated current carrying capacity Iz to be at least 20 A (Reg 433.1.204) and therefore from Table 4D5, Ref Method 101# or, where correction factors (such as grouping or ambient temp) might mess things up a little, Ref Methods A, 100#, 102#.
As per earlier comment re 6 sq mm .... you might struggle with some products to drop spurs off a 4 sq mm ring at a socket-outlet or other accessory to BS 1363 because of terminal constraints if the product meets the minimum requirements of the standard.
Graham, thank you. I see what you mean. I had thought do radial instead, but short of going up to 6 mm² (which as you say, is possible only with the better makes of socket) under those circumstances, it would be necessary either to downsize to a 20 A OCPD, or complete a ring.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site