RCD protection in an IT run office

Former Community Member
Former Community Member
Jolly good morning all,


I am currently carrying out an EICR for an IT based company in their head offices.

Looking at the 12way  3-phase distribution board, I can see there are multiple ‘Office Sockets’ circuits labelled up on 32amp MCB’s and not a single RCD in sight. 

To my knowledge, the use of RCD’s is perhaps not required in this type of environment, but just wanted to check your opinions.


Many thanks you’s and I hope everyone is having a splendid dayV?
Parents
  • Agree, "IT system" has two meanings which appear to have become confused in this case.


    Information Technology ? quite likely in a modern office.

    Or an electrical supply system that is isolated from earth, or floating with no current carrying conductor connected to earth. The opposite of a standard UK system in which the neutral is earthed.


Reply
  • Agree, "IT system" has two meanings which appear to have become confused in this case.


    Information Technology ? quite likely in a modern office.

    Or an electrical supply system that is isolated from earth, or floating with no current carrying conductor connected to earth. The opposite of a standard UK system in which the neutral is earthed.