ARC FLASH IN LOW VOLTAGE MAIN BOARD

Former Community Member
Former Community Member
Hi eveyone ! 


I was wondering if there is a conservative table out there that tells which PPE you should use depending on the voltage, normal current, and shortcircuit perhaps of the place you are working.. 


Specially this is because of a new installation, which will have a main circuit breaker of 2000A, in 400V with a three phase shortcircuit fault of aprox 30KA at the point of the main CB.


When we energise for the first time, what type of PPE should we use ? I have been reading and depends on the cal/m2 but perhaps there was a rapid conservative table or experience of yours to tell what type of PPE we should use 


Also, the main circuit breaker is inside the gabinet, and has no dead front to cover the cooper busbars, they are covered in the front with transparent acrylic (6mm depth), in order to prevent to touch them. So to turn on the MCB we have to do it with the gabinet open
Parents
  • Calculation of incident energy for a specific configuration is problematic , and there is no EN or BSI standard way of doing it at present, which means officially you have little audit trail to say if visor and cotton overalls are more than enough, or at the other extreme if a double brick wall and a bunker is inadequate (common sense suggest somewhere in between).

    For installations in the US, the IEEE publication 1584 (last revised 2018) attempts to assist, by providing formulae that are empirical fits to a number of published experiments involving instrumented tests of deliberate arcs as various parameters change.

    While you need to pay to read the standard itself there is an Excel spreadsheet calculator that anyone who is happy to provide an Email to open a free account can download.

    Having downloaded the spreadsheet, and (as I have IEEE access through work) also read the standard, I must say that I am almost none the wiser as to what actual figures would be applied  to your situation if you were to be using this standard, though there are a number of points worth noting, arcs in enclosures tend to be reflected, so the energy incidence is higher at the open face, than the same distance from an arc free to expand. The corollary of this of course is that it is much better to be to the side of the enclosure, than in the line of fire. The other odd one is that with some 'current limiting' fuses, the arc energy actually drops with increasing PSSC as the disconnection time is faster which is not intuitive.

    As others have said, the best place to be is not there at all - it seems an odd design where the act of switching on requires the only containment to be fully open - I'd expect some sort of inner shield with a cut out around the breaker.

    M.



Reply
  • Calculation of incident energy for a specific configuration is problematic , and there is no EN or BSI standard way of doing it at present, which means officially you have little audit trail to say if visor and cotton overalls are more than enough, or at the other extreme if a double brick wall and a bunker is inadequate (common sense suggest somewhere in between).

    For installations in the US, the IEEE publication 1584 (last revised 2018) attempts to assist, by providing formulae that are empirical fits to a number of published experiments involving instrumented tests of deliberate arcs as various parameters change.

    While you need to pay to read the standard itself there is an Excel spreadsheet calculator that anyone who is happy to provide an Email to open a free account can download.

    Having downloaded the spreadsheet, and (as I have IEEE access through work) also read the standard, I must say that I am almost none the wiser as to what actual figures would be applied  to your situation if you were to be using this standard, though there are a number of points worth noting, arcs in enclosures tend to be reflected, so the energy incidence is higher at the open face, than the same distance from an arc free to expand. The corollary of this of course is that it is much better to be to the side of the enclosure, than in the line of fire. The other odd one is that with some 'current limiting' fuses, the arc energy actually drops with increasing PSSC as the disconnection time is faster which is not intuitive.

    As others have said, the best place to be is not there at all - it seems an odd design where the act of switching on requires the only containment to be fully open - I'd expect some sort of inner shield with a cut out around the breaker.