Zoomup:wallywombat:
Note that zone height is measured from the "floor" of the bath or shower, not the floor of the bathroom.The pictures on page 244 of B.S. 7671 shows the 2.25 metre height as from the room floor. Fig. 701.2
Z.
and the extractor and light are not directly above the bath.. it didn't seem to make much sense to me that a 240v ceiling light was allowed but not a 240v extractor...
Zoomup:wallywombat:
Note that zone height is measured from the "floor" of the bath or shower, not the floor of the bathroom.The pictures on page 244 of B.S. 7671 shows the 2.25 metre height as from the room floor. Fig. 701.2
Z.
and the extractor and light are not directly above the bath.. it didn't seem to make much sense to me that a 240v ceiling light was allowed but not a 240v extractor...