EICR Remedial Work

Former Community Member
Former Community Member
Hi, my first post, I wondered if I could get some advice from the community regarding a failed EICR report and the subsequent remedial works.

Me letting agent appointed a local electrical firm to conduct an EICR report on my flat before new tenants moved in. The timescale was tight since the new tenants were due to move in on the 1st Feb.


The flat is a purpose-built flat constructed in 2005 so id be surprised if the electrics were too far out of spec.


The report came back as failed due to the following points:


1 No Bonding, substantial metal pipework in property

8 Fan is not low voltage in bathroom, and is in zone 2


the quotation for the remedial work was to install 100mm bonding from the consumer unit to the stop cock and replace the extractor with an extra low voltage fan and controller.

"estimate of a morning for 2 which hopefully will be less, however the route is not particularly easy" - £630 inc VAT.


the quote sounded high for a mornings work but due to time constraints i had to agree.


the final invoice came back as 28 hours work, £1399...  so that's 28 hours work to run about 6metres of earth bonding and replace the bathroom fan when the initial quote was a morning's work for £630.


So obviously I've questioned this and after doing some digging, I found that firstly 230v fans are allowed in zone 2, and not all incoming water pipes need to be bonded if there is plastic in the incoming supply..


I'll upload screenshots of the paper work and photos of the job, but any advice would be greatly appreciated!

fef58217ef06411ab3fcb5e012db7a01-huge-quotation.png



b2dc16ff7b1f285e61c95ea8dd664268-huge-eicr-report.png


Parents
  • Former Community Member
    0 Former Community Member
    Big thanks to Chris for taking the time to come and view the installation - I really appreciate the time and effort you've invested in this for me, thank you.


    This evening I decided to purchase an electronic copy of the 18th edition wiring regulation and have been working through the points on the EICR report referencing them back against the 18th edition. 

    Now I'm certainly not an electrician (I'm a financial software developer with a degree in experimental Physics so not a total thickie!) but with help of what Chris said during his site visit, and the 18th edition to refer to, I believe I can now see the blatant (deliberate?) errors in the report. 


    For those wondering, here's a photo showing the location of the ceiling fan - clearly the electrician who conducted the test has a very different understanding of bathroom zones to the rest of us, but he was perfectly happy to install that mains voltage light fitting at the same time as insisting the extractor fan had to be ultra-low voltage... 

    f3f8edf71ea47fbf9a1fbbd095951c71-original-image.png














Reply
  • Former Community Member
    0 Former Community Member
    Big thanks to Chris for taking the time to come and view the installation - I really appreciate the time and effort you've invested in this for me, thank you.


    This evening I decided to purchase an electronic copy of the 18th edition wiring regulation and have been working through the points on the EICR report referencing them back against the 18th edition. 

    Now I'm certainly not an electrician (I'm a financial software developer with a degree in experimental Physics so not a total thickie!) but with help of what Chris said during his site visit, and the 18th edition to refer to, I believe I can now see the blatant (deliberate?) errors in the report. 


    For those wondering, here's a photo showing the location of the ceiling fan - clearly the electrician who conducted the test has a very different understanding of bathroom zones to the rest of us, but he was perfectly happy to install that mains voltage light fitting at the same time as insisting the extractor fan had to be ultra-low voltage... 