Morning gentlepeople of the IET forum.


I'm just throwing this out there to try a get some opinions on cable ferrules and if people use them and where.

From my understanding, they are mainly used during panel builds, IT equipment and even on flexible cables. However, I recently went to a domestic property to perform an EICR and every cable connected to the RCBOs (ignore the earth fly lead which already comes crimped from the manufacturers) had ferrules clamped on the ends.

Clamped on every cable with the exception of the cooker and garage supply, which from memory i believe were both 6mm cables.

in hindsight, i should have taken a picture and shared this, but i didnt, so I failed you all!

To be fair, the electrician who did this, I can see committed to being very neat and tidy. One of the nicest installs i have seen in a while.


I personally have never done this with T+E so just found the ferrule thing a bit strange and wondered if it's something others do, and maybe this could or should be a future reg!?? Pro's and Con's i suppose. 

My thinking was that it does protect the copper cable inside the ferrule, allowing for a better connection too i suppose!?
Parents
  • To avoid inappropriate separation or spreading of individual wires of fine wire conductors, suitable terminals shall be used or ends treated. (BS 7671-526.9.1)


    The photographs below show what happens when fine wire conductors are inadequately captured in the terminals of a 20-amp double pole switch.

    In some cases, it has taken more than five years for the effects to reach maturity.

    Demonstrating this, the photograph below has two types of wiring, with the same cross-sectional area installed into a 20-amp double pole switch.

    Twin and earth supply the switch and heat resistant flex is used as a means of final connection to a water heater.

    The T&E being single solid cores is happy to supply without failure or objection to the load.

    Capturing all the strands of a fine wire conductor in a terminal of this type is very difficult to achieve.

    Multiple outlets were discovered with the same fault, which could have been easily avoided.

    An indicator is cracking of the faceplate caused by excessive heat. Over time it will eventually turn brown.

    Not all terminals are loose!

    2ec0850795e3f12f1e70d7505d1659cc-original-1605446411521.jpg
Reply
  • To avoid inappropriate separation or spreading of individual wires of fine wire conductors, suitable terminals shall be used or ends treated. (BS 7671-526.9.1)


    The photographs below show what happens when fine wire conductors are inadequately captured in the terminals of a 20-amp double pole switch.

    In some cases, it has taken more than five years for the effects to reach maturity.

    Demonstrating this, the photograph below has two types of wiring, with the same cross-sectional area installed into a 20-amp double pole switch.

    Twin and earth supply the switch and heat resistant flex is used as a means of final connection to a water heater.

    The T&E being single solid cores is happy to supply without failure or objection to the load.

    Capturing all the strands of a fine wire conductor in a terminal of this type is very difficult to achieve.

    Multiple outlets were discovered with the same fault, which could have been easily avoided.

    An indicator is cracking of the faceplate caused by excessive heat. Over time it will eventually turn brown.

    Not all terminals are loose!