Fire Alarm Panel Electrical Isolation.

Is single pole electrical isolation suggested here even if we are going to prod and poke about inside the fire alarm panel? And, what are the two fuses removed mentioned all about? Is the lecturer confused?


Please see 41.12 onwards.

https://www.bing.com/videos/search?q=youtube+bs+5839+part+1&&view=detail&mid=92E9069FDA874942E42A92E9069FDA874942E42A&rvsmid=7BBC139314220094A9417BBC139314220094A941&FORM=VDQVAP


Z.
Parents
  • Former Community Member
    0 Former Community Member
    Not watching that too long ? here's what you need to know as far as I'm aware, the OCPD should be on the main board, with relevant markings.  The OCPD should not be of the RCBO/RCD type. 


    At the fire alarm panel you need a double pole FCU with fish tail key or similar, with relevant markings. 


    Regards
    Ts

Reply
  • Former Community Member
    0 Former Community Member
    Not watching that too long ? here's what you need to know as far as I'm aware, the OCPD should be on the main board, with relevant markings.  The OCPD should not be of the RCBO/RCD type. 


    At the fire alarm panel you need a double pole FCU with fish tail key or similar, with relevant markings. 


    Regards
    Ts