AJJewsbury:Well had a look at bs5839:1:2017 and it seems that the mention of a double pole isolator has indeed disappeared!
Which presumably stops it contradicting BS 7671 - where generally N doesn't need isolating on TN systems.
I'd guess that where BS 5839 doesn't override something then normal BS 7671 rules would apply to the supply - so you'd still need DP isolation on a TT system.
- Andy.
I'd agree with your thoughts Andy, bs7671 would be the fallback standard in the case of fire alarm systems. I would also say as a caveat that anything above and beyond the recommendations within a standard I'd also acceptable.
Regards Ts
AJJewsbury:Well had a look at bs5839:1:2017 and it seems that the mention of a double pole isolator has indeed disappeared!
Which presumably stops it contradicting BS 7671 - where generally N doesn't need isolating on TN systems.
I'd guess that where BS 5839 doesn't override something then normal BS 7671 rules would apply to the supply - so you'd still need DP isolation on a TT system.
- Andy.
I'd agree with your thoughts Andy, bs7671 would be the fallback standard in the case of fire alarm systems. I would also say as a caveat that anything above and beyond the recommendations within a standard I'd also acceptable.
Regards Ts