Cable entry metal consumer unit

Hi 


Just a quick query. I have a metal consumer unit to fit and the cables will be entering from the rear. There aren’t many circuits so was planning on having them all entering through one large knockout in the rear. My question is, is it acceptable to have the supply tails entering through the same knockout as the circuit cables or do the supply tails have to enter through a separate hole/knockout?


thanks in advance
Parents
  • Perfectly acceptable, just grommet strip the knockout and if possible use a board with a tail clamp. Would also possibly seal the cable entry as well.
Reply
  • Perfectly acceptable, just grommet strip the knockout and if possible use a board with a tail clamp. Would also possibly seal the cable entry as well.