Cable entry metal consumer unit

Hi 


Just a quick query. I have a metal consumer unit to fit and the cables will be entering from the rear. There aren’t many circuits so was planning on having them all entering through one large knockout in the rear. My question is, is it acceptable to have the supply tails entering through the same knockout as the circuit cables or do the supply tails have to enter through a separate hole/knockout?


thanks in advance
Parents
  • Regs wise just fine, bend radius may mean you may need a larger hole than you think, and plan carefully so you get a layout that does not involve something having an undignified loop the loop around the tails to reach its breaker....

    The other gotcha with entry behind generally is a  wire dropping down the hole and having to be fished out if the wall is hollow partition - depends where exactly things are held captive  -  to have a few P clips or similar at the ready may be helpful if the wall is just partition.

    Mike.