Conduit requirements and cable type

Former Community Member
Former Community Member

I’m in the process of installing seven hard wired fire alarms into our property all of which have to be interlinked.



I intend to re use a now empty steel conduit that runs from right beside our consumer unit up into the loft space. The steel conduit at its point of entry into the loft terminates there presumably the rest was removed in the past. I want to run a cable from there which will have to do an up and over brickwork in the loft.



My first question, is it acceptable in compliance with electrical regulations to simply clip the cable to the brick at the mortar joints or do I have to or even if strictly not necessary should I, put the cable in PVC conduit? This area is not trafficked.



Once I have crossed the brick work and come down to the first alarm, from there I intend to run a cable down the near center of the loft adjacent to the walkway in pvc conduit parallel to the 2 existing lighting circuit conduits located above the joists. I am not going to drill through the joists. At points along the conduit there will be junctions to allow clipped cable not in conduit to be ran parallel to the joists to the relevant alarm. The conduit is going to be a straight run, so my question is having consulted a few sources that state 1.5mm flexible cable not twin and earth must be used in conduit, does it? I understand the reason for flexible cable in conduit with a lot of turns and junctions but this is a straight run.


Thanks


Parents
  • It is normal to use red FP200 for fire alarms, andit  is reasonably priced and well mechanically protected, even rats don't like it much, and fireproof! If these are just the detectors (and just single dwelling domestic) you may be happy with something less, but singles in conduit cost more than FP200 and are far less tidy. I suspect you are in an HMO because the double board is for fire protection, so you will need all the bits and pieces including an alarm panel and fire buttons, to give firemen a guide to the fire zones and 7 smoke alarms are quite a lot!. If so you will need some professional advice.
Reply
  • It is normal to use red FP200 for fire alarms, andit  is reasonably priced and well mechanically protected, even rats don't like it much, and fireproof! If these are just the detectors (and just single dwelling domestic) you may be happy with something less, but singles in conduit cost more than FP200 and are far less tidy. I suspect you are in an HMO because the double board is for fire protection, so you will need all the bits and pieces including an alarm panel and fire buttons, to give firemen a guide to the fire zones and 7 smoke alarms are quite a lot!. If so you will need some professional advice.