Fred down the pub said that I can save money by not using a qualified sparks to test my R.C.Ds. He said that I can make my own R.C.D. tester. Is it safe? 

How to make RCCB tester at Home - YouTube


Z.
Parents
  • Denis McMahon:

    In a word - no!


    You can't use any old light bulb as an earth leakage test. You need to consider the minimum trip current specified. The test device must draw this minimum current, so the resistive element must be suitably chosen.


    Yes but it does work, and the R.C.D. trips off  very quickly. Reg. 643.8 says that a current equal to, or higher than, five times the R.C.D's rated residual operating current is required for the test. So a 15 Watt lamp will provide this.


    Z.


Reply
  • Denis McMahon:

    In a word - no!


    You can't use any old light bulb as an earth leakage test. You need to consider the minimum trip current specified. The test device must draw this minimum current, so the resistive element must be suitably chosen.


    Yes but it does work, and the R.C.D. trips off  very quickly. Reg. 643.8 says that a current equal to, or higher than, five times the R.C.D's rated residual operating current is required for the test. So a 15 Watt lamp will provide this.


    Z.