So an isolator isn’t for emergency switching as it requires two steps?
Table 537.4 allows a BS EN 60947-3 switch for emergency switching, but it is the normal 100 D.P. switch as found in many consumer units. I would not choose it as a first choice for an emergency stop switch for an industrial machine application. I would use the red mushroom head with a yellow background that once activated locks off as my first choice connected through suitable circuitry.
Z.
MrJack96:
So an isolator isn’t for emergency switching as it requires two steps?
Table 537.4 allows a BS EN 60947-3 switch for emergency switching, but it is the normal 100 D.P. switch as found in many consumer units. I would not choose it as a first choice for an emergency stop switch for an industrial machine application. I would use the red mushroom head with a yellow background that once activated locks off as my first choice connected through suitable circuitry.
Z.