IP rating for roof panel

Hello,

In a commercial office building there is a roof panel which mainly feeds the condenser units. The IP rating of the panel is 55. 


Usually I have come across IP65 panels when they re installed outdoors.


While I understand the difference between the two, I cannot find any regulations that would require the panel to be IP65 instead of IP55. 


Thus, as long as the panel supplier confirms that the panel is suitable for use outdoors I believe it should be fine?


For the record, there is no specific requirement stated in the consultant specifications.


It would be appreciated if you could share your thoughts


Thank you
  • As the water ingress is the same I can't see an issue
  • Hi Dbat, thanks for your response.


    Is it the case that an IP56 or IP66 could be required?


    Do you know any regs that I can refer to in order to substantiate the appropriate IP rating for a panel installed at the roof?
  • For most situations BS 7671 doesn't specify particular IP rating - but rather that equipment should be "suitable" for the environment (e.g. reg 512.2).


    The problem is that what's suitable for one situation might be quite inadequate for another - a roof of a sheltered inland building could probably get away with a lot lower IP rating than say the roof of a lighthouse on the coast or a building atop a high exposed mountain.


    Appendix 5 of BS 7671 gives some guidance - specifically sections AD and AE for IP ratings. If the worst is normal rain then IPX4 or even IPX3 might be entirely suitable. IPX5 or IPX6 would only normally be required where jets of water would be expected (so paradoxically perhaps more likely to be needed at low levels where pressure washers might be used rather than high out of the way places exposed to 'just' the weather).


    The 1st digit - for protection against solids - particularly dust for IP5X or IP6X - both provide adequate protection for the contents of the enclosure - either by ensuring no dust at all gets in, or by only allowing in quantities that won't cause a problem. So unless it's a particularly sensitive equipment, or an extraordinary challenging situation, it's probably not a deal breaker either way.


      - Andy.