Garage/Outbuilding electrical installation

Former Community Member
Former Community Member
I have two garages that are separate buildings from my house. Currently there is a 100A incoming fuse protecting my split load consumer unit. Circuits are divided across the two 80A 30mA RCDs and protected by appropriate individual MCB's. The consumer unit was installed in 2011 and three circuits were installed before the RCD off the main switch, each protected by an MCB. These circuits were 6A - Burglar Alarm, 20A - fridge freezer, 40A - Garage no.1 supply. The garage no.1 had a consumer unit install with a 60A main switch with two circuits coming off of it, 6A MCB - lighting, 16A RCBO - Socket outlets (all circuits in this garage are contained in steel conduit). The supply from the 40A MCB in the main consumer unit to the garage no.1 consumer unit is 10mm SWA 8 metres in length.

In 2017 a second garage was built on a plot of land behind the first garage (an alley way separates the two). A 10mm SWA was run from garage no.1 to garage no.2 a distance of 10 metres between garages. installed in a duct in order to cross the alley way.

Garage no.2 had a consumer unit installed with a 60A main switch, the 10mm SWA supplying the board is daisy chained from the main switch of garage no.1. All circuits from this board are installed in pvc conduit and bench trunking. There is a circuit feeding an outside socket which is protected by a 16A RCBO. All other circuits are protected by MCB's, but all sockets within the garage are RCD socket outlets.


I have two questions;


1. Do i need to install earth electrode and create TT supply at the first garage? i did read that maybe this was not a requirement as the SWA is 10mm 3core and therefore the size of the earth to garages is the same as the earth bonds at the house.


2. Do i need to install more RCD protection? At the house to protect the 10mm SWA feeding both garages? and at both garages after main switches to protect all the circuits? Could i install a 40A 100mA RCD at the house so i get discrimination of the RCD's?


  • I'm not clear why you think you need to change anything at all - is there a specific problem?


    You do not say how your house is earthed - I assume some DNO supplied earth terminal, so the MCBs covering the alarms and so on would operate OK with an fault to earth. IF they were installed today those would probably be RCBO (*) not MCB

    However, if the garage supply requires RCD cover or not rather depends on the cable arrangements. Cables like SWA with an earthed armour, or an external equivalent, like earthed metal trunking or conduit over a soft skinned cable, do not need RCD protection. The assumption is that any misplaced drill or pick axe or whatever, will be earthed by the armour, or the conduit, and when it reaches the live core there will be a flash and a pop, but the  fuse or breaker will be enough  to disconnect, as the prospective fault current will be many hundreds of amps.

    In your case it sounds like  it is an armoured cable, on a supply with a hard wired earth, so no RCD is needed at the origin.

    Note that if any part of the run was in twin and earth (or any similar cable without an earthed armour) in a route that is not either obvious (from the surface), or more than 50mm from the wall or floor finish, so serious tools wouldlbe needed to damage it by mistake, then it would need RCD protection after all..

    In the garage itself you may prefer there to be the RCD there, rather than run back to the house if it goes dark.

    If you want to add RCD cover to the wiring in the garage itself, (perhaps that is soft skinned cable ?)  then changing the local CUs main switch for an RCD may be easiest.

    You do not need to make the garages into a TT island, unless you have things in the garage that require it - a car charging point or socket for  a  caravan would be classics, or indeed if you had a ham radio station you might like it, if antennas are the kind that are outdoors and need a large earth electrode (VHF ones that look like TV antennas do not normally).

    If your garage had running water coming in metal pipes then a 10mm bond is needed back to the house if you are using the house earth, but you have that anyway.


    regards mike.


    * An RCBO, combines RCD and MCB functions, and senses overloads as well as earth faults- an RCD does not sense overload, just L-N imbalance to detect earth faults, and needs further MCBs or fuses to handle the overload case.


    PS a standard 40A RCD is still looking for a 30mA difference current, so unless it is s time delay type, it will race with any 30mA RCD further downstream so either or both may trip - to discriminate reliably you need special time delay RCDs, - usually set up in cascades in factors of 3

    A possible example of a robust system where faults trip out only the minimum of circuits,  may be a 300mA RCD with 1/3 second delay, feeding a few branches each with 100mA RCD with 0.1sec delay ('S type') feeding final circuits each with instant 30mA types for personal protection. Normally in domestic, it is not worth that level of complexity.


  • The only thing I think I can add to Mike's is to note that the latest regulations do ask for 30mA RCD protection for domestic lighting circuits (in addition to the usual requirement for soft-sheathed cables concealed in walls, serving bathrooms etc) - so that does sound to be one point where the current arrangement falls slightly short. It is quite a minor deviation however and wouldn't normally require fixing unless you were making a change to the circuit - it wouldn't result in anything more than a C3 on an EICR for example.


      - Andy.