Electrical Testing

Former Community Member
Former Community Member
When coding any consumer unit or switchgear with a combustible (plastic) enclosure only when it is located under a wooden staircase or within a sole route of escape, a C3 is recommended. 


Does this recommendation signify that the overall rating of the install be satisfactory or unsatisfactory? 


I have been ticking Unsatisfactory for the general condition of the installation (in terms of electrical safety) AND the overall assessment of the installation in terms of its continued use! 


Is wrong wrong of me? Even though everything is perfect with results and the installation?
Parents
  • John Peckham:

    Afternoon Chris


    I don't think so look at the Notes for the Report on Page 475 para 9 of the Big Blue Bumper Book of Fun.


    I am not disagreeing with you. I agree that the note makes it pretty clear.


Reply
  • John Peckham:

    Afternoon Chris


    I don't think so look at the Notes for the Report on Page 475 para 9 of the Big Blue Bumper Book of Fun.


    I am not disagreeing with you. I agree that the note makes it pretty clear.