Well if you need RCD protection on single phases independently of the two other phases then then yes 3 x RCD (RCCB) i.e 1 per phase or better still each MCB to be an RCBO (an RCCB & MCB combined in one unit) instead. If you have any actual 3 phase loads then you need a 3P+N RCD (RCCB) for that circuit only. Not for any single phase circuits.
ebee. I have 3x Three Phase Circuits (13A, 40A, 48A). I wish to protect EACH Three Phase Circuit independently with RCCBs. Was hoping to avoid the £444 (MCG Industry) cost of the 13A, 40A, 50/63A 3 Pole RCBOs. Wylex 4P RCCBs & 3P MCBs come to £180 approx. Cheers.
ebee:
Well if you need RCD protection on single phases independently of the two other phases then then yes 3 x RCD (RCCB) i.e 1 per phase or better still each MCB to be an RCBO (an RCCB & MCB combined in one unit) instead. If you have any actual 3 phase loads then you need a 3P+N RCD (RCCB) for that circuit only. Not for any single phase circuits.
ebee. I have 3x Three Phase Circuits (13A, 40A, 48A). I wish to protect EACH Three Phase Circuit independently with RCCBs. Was hoping to avoid the £444 (MCG Industry) cost of the 13A, 40A, 50/63A 3 Pole RCBOs. Wylex 4P RCCBs & 3P MCBs come to £180 approx. Cheers.