What you draw is OK for a system where 3 phase comes in, but all loads are single phase. In effect you have drawn 3 single phase consumer units - and that is one legitimate approach, if your loads are like that.
3 phase boards for 3 phase loads have a 3 pattern L1 L2 L3 bus bar so every tooth is only connected to the ones multiples of 3 places along.
. And just to catch you, L and N (pitch of two) and 3 phase and neutral (pitch of 4 ) busbar is also manufactured but rarer.
an RCD for a 3 phase load must carry all the phases, and neutral if there is one, so that in normal use, it sees no net current.
I suggest you contact the helplines of one of the makers of commercial consumer units (Hagar, Eaton etc) to advise you about what they make, as there are a lot of options, and it is very easy to specify the wrong thing, the advice is free, so long as you do not string them along..
Are the loads in your drawing correct, or just nice numbers ? Thinking diversity.
M.
Thanks M,
Ah understood. It isn't my drawing by the way, just something I found on the web.
You've lost me a little with the Busbar info???...
Was just trying to understand if it is possible to connect/wire up 4P RCCBs and 4P MCBs on a DIN Rail in the same manner as a 1P RCCBs and numerous 1P MCBs can be? i.e. By connecting the L1 L2 L3 of the 4P RCCB to the L1 L2 L3 of the 4P MCB via a busbar or individual wiring.
Only 3 Circuits of the 3-Phase Distribution Board will be feeding 3-Phase gear. Rest of the gear will be single phase.
Circuit 1 - 48A - feeding a Control Panel which in turn will be switching 4x individual 3-phase Immersion Elements.
Circuit 2 - 40A - feeding a 3-phase Instant Hot Water Heater.
Circuit 3 - 13A - feeding a 3-phase Pump.
Trying to avoid RCBOs or RCCB Sockets as these are pricey options. Will have to go this route if need be though!
Cheers.
Apologies for any confusion. I do intend to use brand new components from the same manufacturer. Probable Wylex in this situation.
Was just trying to understand if it is possible to connect/wire up a 4P RCCB and a 4P MCB in the same manner as a 1P RCCB and numerous MCBs? i.e. By connecting the L1 L2 L3 of the 4P RCCB to the L1 L2 L3 of the 4P MCB via a Busbar or Individual wiring of L1 L2 L3?
mapj1:
no -it isn't you need a box fitted with a proper 3 phase busbar, which is really 3 or 4 isolated busses in one block
Each maker has (slightly incompatible) variations on the theme.
Ah I see! ? Are these adjustable length wise like normal Busbar's? Thanks for sharing.
AJJewsbury:Apologies for any confusion. I do intend to use brand new components from the same manufacturer. Probable Wylex in this situation.
Was just trying to understand if it is possible to connect/wire up a 4P RCCB and a 4P MCB in the same manner as a 1P RCCB and numerous MCBs? i.e. By connecting the L1 L2 L3 of the 4P RCCB to the L1 L2 L3 of the 4P MCB via a Busbar or Individual wiring of L1 L2 L3?
It's not just a matter of using components from a single manufacturer if you want to rely on their type approval - you have to assemble it according to their instructions ... which they likely don't have for anything not based on their normal layouts (but feel free to ask them of course).
In terms of wiring, in theory it is that simple - in practice a 3-phase MCB will usually have 3 pairs of terminals and a 3-phase RCCB will have 4 pairs (to include the N) - so simple bus-bars won't usually fit... you could then go for simple bits of wire between, but then you've got the problems of fault handling etc. that the bus-bars were probably designed to avoid (especially if you're relying on the type-test for a 16kA or better fault rating or the assembly). 3-phase MCBs that also include a N would be simpler, but they're rarer beasts (especially when it comes to actually buying one rather than just perusing catalogues) and then you'd need 4-P bus-bars which can be rarer still in the UK. Not impossible, but I'd advise a fair amount of caution. Be especially careful of examples of 'continental' practice from the internet - the UK supply system has a few characteristics (in particular a relatively high protective fault current - due to our approach of supplying relatively large loads single phase) that demands a bit more consideration that is needed elsewhere where the higher impedance of lower rated 3-phase supplies is the norm.
- Andy.
Cheers Andy. So it's possible but not normal practice or layout? Have you ever seen it done? Or are RCCBs nearly always downstream? Or a RCBO used?
Cheers Andy. So it's possible but not normal practice or layout? Have you ever seen it done? Or are RCCBs nearly always downstream? Or a RCBO used?
mapj1:
But a 3 phase RCBO with neutral is harder, as really you need a 4 pole bus bar, and that is not so common, though I suppose it will come, after all we've only had RCDs in common use for about 40 years now.
Eh? TPN RCBO takes up 4 (SP) ways with N sitting over one of the phases and a pigtail to the N bar.