Hi guys I have seen an isolating transformer feeding a single phase pump on site and am unsure if it should be isolated. I can see they have tied the 0v on the 110v side to earth just not the 240v Can anyone give me some advice. Here are some pictures.
I presume it is a 110V pump with a controller that needed a supply with a live and a neutral 110V apart, rather than the centre earthed 55-0-55 that you often get given in the UK when you ask for 110V .
As such, if that is the case, it is a perfectly good way to do it, assuming the wattages are OK and it runs cool.
I presume it is a 110V pump with a controller that needed a supply with a live and a neutral 110V apart, rather than the centre earthed 55-0-55 that you often get given in the UK when you ask for 110V .
As such, if that is the case, it is a perfectly good way to do it, assuming the wattages are OK and it runs cool.