This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

3 phase motors

I’ve got two questions regarding maintenance on motors. The first one is is there any hazards lubricating a motor in service I know obviously there will be mechanical safety to be aware of but electrical is there any issues. 


my second question is with motor overloads how bad for the motor is having a 1.8amp 10a overload on a motor with 1.75FLC I know it can still be overloaded by 50ma but is it a concern. 


thanks again guys!
Parents Reply Children
No Data