Chris Pearson:
I have previously been put in my place here by GK, the pair is rated at 13 A.
That said, we have had washing machine and tumble drier plugged into one double socket and kettle and toaster into another for 20-odd years. Not always one load of clothes out and another in whilst the first are dried; but every breakfast time the bread is toasted whilst the kettle is on. No harm done! ?
IMHO, the bottom line is that Joe Public would rightly expect to put 13 A in both sides.
These days, even manufacturers who said "13 A per outlet" in their literature now say "13 A" full stop. There may well always have been some confusion between whether "socket-outlet" referred to a single or double version, and we still call a double socket-outlet a single "point".
Certainly, the temperature rise test now is no different than it was back in 1984, perhaps even earlier ... but it's worth noting that the temperature rise test has a maximum duration of 8 hours, so it is not really intended to simulate repeated overload of the accessory, just a one-off occurrence lasting a single typical "working day"
broadgage:
A sustained 26 amp load is very unlikely as apart from kettles, very few modern domestic appliances use more than about 10 amps.
A total 20 amp load is quite likely, a tumble dryer and a space heater for example.
Kettles are sometimes a full 13 amps, but seem fine in practice due to the short term use.
How many minutes does a domestic kettle take to boil water?
Z.
I understood that twin 13 amp sockets are designed for a total load of 20 amps, and that the approval test is done with 14 amps one one side and 6 amps on the other side.
However recent posts on these fora and elsewhere have stated or implied that the maximum permitted load is only 13 amps in total.
So which is it ?
AJJewsbury:I understood that twin 13 amp sockets are designed for a total load of 20 amps, and that the approval test is done with 14 amps one one side and 6 amps on the other side.
However recent posts on these fora and elsewhere have stated or implied that the maximum permitted load is only 13 amps in total.
So which is it ?
i don't see why both can't be true - it's not unusual for tests to be somewhat in excess of nominal rating in order to allow a decent margin of error/safety. IIRC lifting gear has to pass a test of at least 2x its stated capacity.
- Andy.
Just as a socket-outlet has a temperature rise test, so does the plug
In the test for a double socket-outlet, one of the plugs is not sufficiently loaded to achieve what could (in a fully loaded plug) be 37 K temperature rise at the plug pins - but the other is.
Quite simply, reliance on the product standard alone, in its present form, can't demonstrate that the double socket-outlet is suitable for 2 no. plugs each pulling 13 A.