EICR - Old Rewireable Fuse boards are these acceptable?

Former Community Member
Former Community Member
Hi, 


I need verification that it is ok to keep old style Wylex rewireable fuse boards to pass the EICR. Initially the electrician said this was ok providing they have a cover for the fuses. However he has now changed his mind and saying they need to be replaced with a new consumer unit. Some of the homes do not have a cover on the fuse board and others have had the cover taken off so plug in mcb's can be accomodated. Is this still ok?
Parents
  • There's nothing in principle wrong with BS 3036 fuses - they're still specifically listed as acceptable in today's regulations (along with the diameter of tinned copper fuse wire to use).


    On their own however they're likely to be lacking modern facilities - such as 30mA RCDs or perhaps SPDs. These however could be added as in separate enclosures if required.


    Lack of 30mA RCD additional protection is likely to be a C3 in most cases - but can be a C2 for things like sockets likely to feed equipment outdoors or for bathroom circuits together with a lack of supplementary bonding for instance.


    The lack of a cover over the fuse carries isn't ideal - they are after all only semi-enclosed and so arc products can be ejected from them if a fuse blows (hence the warning to switch off before handling fuses embossed into most of them) - but even then I probably wouldn't go for a C2 unless it was in a particularly flammable area. Where the fuse wire carriers have been replaced by plug-in MCBs I think it's less of an issue.


        - Andy.
Reply
  • There's nothing in principle wrong with BS 3036 fuses - they're still specifically listed as acceptable in today's regulations (along with the diameter of tinned copper fuse wire to use).


    On their own however they're likely to be lacking modern facilities - such as 30mA RCDs or perhaps SPDs. These however could be added as in separate enclosures if required.


    Lack of 30mA RCD additional protection is likely to be a C3 in most cases - but can be a C2 for things like sockets likely to feed equipment outdoors or for bathroom circuits together with a lack of supplementary bonding for instance.


    The lack of a cover over the fuse carries isn't ideal - they are after all only semi-enclosed and so arc products can be ejected from them if a fuse blows (hence the warning to switch off before handling fuses embossed into most of them) - but even then I probably wouldn't go for a C2 unless it was in a particularly flammable area. Where the fuse wire carriers have been replaced by plug-in MCBs I think it's less of an issue.


        - Andy.